Question : Problem: Failed to apply the configuration profile

I have an APC UPS attached to the server. I installed PowerChute software and when I have to add the a device to the list a receive and error:Failed to apply the configuration profile to server...
I tried reinstalling the software, but with no success. I have attached a snapshot of the error.

Answer : Problem: Failed to apply the configuration profile

how are you connecting to the UPS?  via network?  If so then you are trying to install the wrong version.
PowerChute Network Shutdown is the correct software. Uninstall Business Edition and download the network edition from the following link:

http://www.apc.com/tools/download

If you are connecting via serial, or USB then check then the answer may be in this article from the APC website:

There are several reasons PowerChute Business Edition will return this error.

Issue1:

If the user name and password given to the PowerChute Business Edition Agent do not match those given to the PowerChute Business Edition Server.

Solution:

Log into the Server through the Console application and go to the Tools menu and change user name and password. This will only work on PowerChute Business Edition version 6.1 or higher. This will also change the user name and password for all Agents already configured with this Server.

Uninstall the Agent portion of the software and reinstall with a user name and password that matches the Server.

Issue 2:

An unsupported UPS will give this error as well. Powerchute Business Edition only supports currently manufactured Smart UPS units, Matrix with Rev Z firmware, Back UPS Pro S models and Powerstack in Smart signaling. Back-UPS, Back-UPS Pro PNP, Back-UPS Pro, Smart-UPS V/S, and the Interface Expander are supported as well in Simple signaling mode only with the APC Simple signaling DB9 serial cable (part number 940-0020B or C).

Solution:

Upgrade to a supported UPS model. This can be done through APC's Trade UPS program, http://www.apcc.com/buy/

Uninstall the Powerchute Business Edition software and use Powerchute Plus software.

Issue 3:

No Network communications between the Agent and Server can cause this issue as well. Firewalls or a lack of a proper network configuration can be the cause

Solution:


If the Server portion is installed on a different system than the Agent, try to ping the Agent’s system from the Server’s system. If the system cannot be pinged, there is a network issue that must be resolved before PowerChute can apply the configuration profile. To ping another system, simply go to a command prompt and type the following: ping agent_ip where agent_ip is the ip address of the system with the Agent installed.


If the network has a firewall, this can be the source of the communications issue. Make sure ports 3052, 2260, 2160, and 2161 are not blocked. Some Anti-Virus software can block ports and can install a firewall. There have been some cases where Anti-Virus software has had to be stopped or uninstalled and then the Business Edition Agent reinstalled to solve this issue. In most cases, the Anti-Virus software could then be restarted or reinstalled. PCBE ports used and protocols: 2161 - TCP & UDP 2160 - TCP 2260 - TCP & UDP 3052 - TCP Security used: logging into agent through server SSL logging into server through console MD5


If the system where the Agent is installed has more than 1 network card, the PowerChute Business Edition Server may not be able to locate the Agent. If this is the case, check TCP/IP properties for it’s binding order. Make sure the IP of the card you are adding to the configuration is the first item in the TCP/IP binding order.


Make sure TCP/IP is installed properly and the network card is bound


If the system does not have a network card or is not on a network, it will be necessary to install Microsoft’s Loop-Back Adapter. This will allow you to type 127.0.0.1 in place of the actual system IP. The loop back adapter must be installed on systems that are not on a network if the Agent is to be accessed through a browser as well.


A DMZ (demilitarized zone) is similar to a firewall. In this type of situation, the Agent and Server may not be able to achieve 2 way communications. If there is an issue such as this, you can open the same ports as listed for a firewall but we recommend simply making sure the Agent and Server reside on the same side of the DMZ.

Issue 4:

If you are using a USB Smart UPS unit and the USB cable is connected to the keyboard hub or an external hub.

Solution:

Disconnect the USB cable from the keyboard hub or external hub and connect it directly to the root hub in the PC

Issue 5:

The Agent service is not running.

Solution:

As above, try to connect to the Agent through it’s web user interface. If you cannot connect, the Agent may not be running. In NT, go Control Panel and Services. In Windows 2000 or Windows XP, go to Control Panel, Administrative Tools, Services. Make sure the APC PBE Agent service is started and set to automatic.

Issue 6:

The Agent is Running, The Agent is communicating, Network is Set Up Properly

Solution:

Some Version of Antivirus Software have a built in firewall. The Firewall is not something the user normally has to configure. If you stop the AntiVirus Software from running and then try to apply to configure profile again. Once the setup complete and the Configuration profile is applied. Simply start the Antivirus software again.